    Choosing a 3 Phase AC Current Sensor for Motor Monitoring

    5 months ago
    #359 Quote
    Hey everyone,

    I’m a research assistant at a university, working on a project where I need to measure AC current on a 3-phase cable supplying an electric motor. The measured current data will be sent to a microcontroller. Since I’m a mechanical engineer with limited experience in electronics, I could use some advice on selecting a suitable sensor.

    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?
    0
    5 months ago
    #360 Quote
    William wrote:
    Hey everyone,

    I’m a research assistant at a university, working on a project where I need to measure AC current on a 3-phase cable supplying an electric motor. The measured current data will be sent to a microcontroller. Since I’m a mechanical engineer with limited experience in electronics, I could use some advice on selecting a suitable sensor.

    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?
    Based on your requirements, I'd recommend the ATO-CUS-3AC80 model. It measures up to 80A with 0.5%FS accuracy, which should work well within your typical range. Let us know if you have any other questions!
    0
    laisteel.com
    5 months ago
    #361 Quote
    William wrote:
    Hey everyone,

    I’m a research assistant at a university, working on a project where I need to measure AC current on a 3-phase cable supplying an electric motor. The measured current data will be sent to a microcontroller. Since I’m a mechanical engineer with limited experience in electronics, I could use some advice on selecting a suitable sensor.

    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?
    The ATO-CUS-3AC80 looks fine for your steady-state currents, but your startup current of 450A is a concern. If the sensor saturates at 80A, it won't capture the inrush current properly. If startup current monitoring is critical, you might need a sensor with a higher range, or a dual-sensor setup—one optimized for normal operation and another for startup conditions.
    0
    5 months ago
    #362 Quote
    ATO wrote:
    Hey everyone,

    I’m a research assistant at a university, working on a project where I need to measure AC current on a 3-phase cable supplying an electric motor. The measured current data will be sent to a microcontroller. Since I’m a mechanical engineer with limited experience in electronics, I could use some advice on selecting a suitable sensor.

    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?Based on your requirements, I'd recommend the ATO-CUS-3AC80 model. It measures up to 80A with 0.5%FS accuracy, which should work well within your typical range. Let us know if you have any other questions!
    Thanks for the insights! That helps a lot. I do have one more question about the "overload capacity" listed in the datasheet. It says "30 times nominal input." Does this mean the sensor can handle up to 2400A for a short time? If so, how long can it withstand that overload?
    0
    5 months ago
    #363 Quote
    William wrote:
    Thanks for the insights! That helps a lot. I do have one more question about the "overload capacity" listed in the datasheet. It says "30 times nominal input." Does this mean the sensor can handle up to 2400A for a short time? If so, how long can it withstand that overload?
    Good question! The overload capacity refers to the sensor's instantaneous limit. It can handle up to 2400A for a very short duration—about 4-5 seconds max before potential damage occurs. It's not meant for continuous operation at those levels.
    0