    How to Fix E-03 and E-12 Errors on My 15 hp VFD?

    27 days ago
    #492 Quote
    Hello all,
    We recently installed an ATO 15 hp VFD on our press machine. It worked fine right out of the box without changing any parameters — just plug and play. However, the next day, we started getting E-03 (overcurrent) and E-12 (output phase loss) errors. This is critical because the press must be operational for production. Has anyone run into this before?
    15 hp VFD link: https://ato.laisteel.com/15hp-single-phase-to-three-phase-vfd
    0
    27 days ago
    #493 Quote
    Wexley wrote:
    Hello all,
    We recently installed an ATO 15 hp VFD on our press machine. It worked fine right out of the box without changing any parameters — just plug and play. However, the next day, we started getting E-03 (overcurrent) and E-12 (output phase loss) errors. This is critical because the press must be operational for production. Has anyone run into this before?
    15 hp VFD link: https://ato.laisteel.com/15hp-single-phase-to-three-phase-vfd
    Hi Wexley,
    Here’s what those errors mean:
    1. E03 means the VFD is running over the current.
    Please check whether the VFD input voltage is abnormal, and pay attention to set the acceleration and deceleration time P0.12=10 or 15 (acceleration time 15s), P0.13=10 or 15 (deceleration time 15s)
    2. E12 means that the VFD output terminal is out of phase.
    Please check whether the cables connecting the VFD output terminals U, V, and W to the motor are loose. Or if the cable is damaged, test again.
    If the issue persists, please send a photo of the VFD and motor nameplate showing the issue.
    2
    laisteel.com
    27 days ago
    #495 Quote
    ATO wrote:
    Hi Wexley,
    Here’s what those errors mean:
    1. E03 means the VFD is running over the current.
    Please check whether the VFD input voltage is abnormal, and pay attention to set the acceleration and deceleration time P0.12=10 or 15 (acceleration time 15s), P0.13=10 or 15 (deceleration time 15s)
    2. E12 means that the VFD output terminal is out of phase.
    Please check whether the cables connecting the VFD output terminals U, V, and W to the motor are loose. Or if the cable is damaged, test again.
    If the issue persists, please send a photo of the VFD and motor nameplate showing the issue.
    Thanks. We tried that. The VFD still trips on E-03 after about 4 cycles of the motor. I've attached a photo of the motor nameplate for reference.


    0
    27 days ago
    #496 Quote
    Wexley wrote:
    Thanks. We tried that. The VFD still trips on E-03 after about 4 cycles of the motor. I've attached a photo of the motor nameplate for reference.


    Thanks. We reviewed the motor nameplate — it supports 220/380/440V. Your VFD outputs 220V 3-phase, so please confirm the motor is wired for low-voltage 220V operation.
    Additionally:
    1. Disconnect the motor and inspect for shorts or damage.
    2. Try running the VFD unloaded (no motor attached) to see if it still throws E-03.
    3. With a multimeter, check for 220V between U-V, V-W, and W-U during operation.
    4. If it runs fine without load, your motor may be miswired or faulty.
    2
    laisteel.com
    27 days ago
    #497 Quote
    ATO wrote:
    Thanks. We reviewed the motor nameplate — it supports 220/380/440V. Your VFD outputs 220V 3-phase, so please confirm the motor is wired for low-voltage 220V operation.
    Additionally:
    1. Disconnect the motor and inspect for shorts or damage.
    2. Try running the VFD unloaded (no motor attached) to see if it still throws E-03.
    3. With a multimeter, check for 220V between U-V, V-W, and W-U during operation.
    4. If it runs fine without load, your motor may be miswired or faulty.
    Confirmed — we’re using 220V single-phase input, and the motor is wired correctly for 220V 3-phase. Still getting E-03 after a few operations.
    2
    27 days ago
    #498 Quote
    Wexley wrote:
    Confirmed — we’re using 220V single-phase input, and the motor is wired correctly for 220V 3-phase. Still getting E-03 after a few operations.
    Thanks for confirming. Please:
    Record the startup current shown on the VFD panel. If it exceeds the VFD’s rated current, the load may be too high or a mismatch. Again, try running the VFD without the motor to isolate the issue.
    1
    laisteel.com
    27 days ago
    #499 Quote
    I just want to chime in and say I completely agree with ATO's recommendations. We had a similar case on-site where the VFD kept throwing E03 errors. It turned out the acceleration time was too short, causing a spike in current. In another instance, the motor was wired for the wrong voltage setting — visually, everything looked fine, but the internal wiring was incorrect.

    ATO’s step-by-step approach, especially the no-load test, really helps narrow things down. I strongly recommend OP follow their advice and record the startup current — that detail can make all the difference in identifying the real issue.
    0
    27 days ago
    #500 Quote
    Appreciate the suggestions! We’re going to record the startup current and test the VFD unloaded!
    0